Export V7.1 lightshow to V9 to Rack1024

usb to dmx - 1024 dmx channels - 19'' rack - 16 flash buttons - IR remote controller - 8 external contacts - calendar
support
Administrateur
Posts: 10756
Joined: 07 December 2009, 16:32

Re: Export V7.1 lightshow to V9 to Rack1024

Post by support »

We analysed the lightshow.
V9 crashes when opening the existing converted V7 scenes.
And V9 is not able to convert the old V7 scenes correctly.
We did not find any solution to fix that.
It will not be possible to get the V7 scenes for V9.
Sorry for that.
The Lighting Controller
Niffo
Administrateur
Posts: 725
Joined: 07 December 2009, 15:59

Re: Export V7.1 lightshow to V9 to Rack1024

Post by Niffo »

Hello bandaribeiro,
We have checked your Lighshow and found that for some unknown reason the ".scex" files located in the "scenes" directory are corrupted (binary files filled with 0s!).
Please delete all ".scex" files (not ".sce" files) located in this directory and its subdirectories, then relaunch the latest Sweetlight version 9.